Electricity is distributed from electrical substations to neighborhoods at 1.3×104 V . This is a 60Hz oscillating (AC) voltage. Neighborhood transformers, seen on utility poles, step this voltage down to the 120V that is delivered to your house. No energy is lost in an ideal transformer, so the output power Pout from the secondary coil equals the input power Pin to the primary coil. Suppose a neighborhood transformer delivers 300 A at 120 V. What is the current in the 1.3×104 V line from the substation?
Explanation / Answer
since no energy lost in transformer so effieciency is 100%
hence
input power = ouput power
Pi = Po
let v1 be the voltage across primary coil
i1 be current through primary coil
V2 be the voltage across secondary coil
i2 be the current through secondary coil
v1 i1 = v2 i2
1.3*104 V * i1 = 120V (300A)
i1 = (120V)(300A) / (1.3*104 V) = 2.769 A