9. A manufacturing plant has a 600V, 60Hz supply and the following loads: Lights
ID: 1813123 • Letter: 9
Question
9. A manufacturing plant has a 600V, 60Hz supply and the following loads:
Lights: 24kW
Electric furnace: 4.8 + j6.4%u03A9 with a current of 150A
Motor loads, 160kW at 0.8 Power Factor, lagging.
The total real power PT is
24 KW
108 KW
184 KW
292 KW
10. For the conditions in question 9, what is the total reactive power QT?
120 kVARS
144 kVARS
264 kVARS
592 kVARS
11. For the conditions in problem 9, what is the total apparent power S?
264 kVA
318 kVA
394 kVA
421 kVA
a.24 KW
b.108 KW
c.184 KW
d.292 KW
Explanation / Answer
9)Pt = total power = 24 + 150^2*2.8 +160 = 292 kw
10) Reactive power = 150^2*6.4 + 160(1-0.8^2)60.5/0.8 = 144 + 120 =264 k VARs
11.)total apparent power = [292^2+264^2]]^0.5 =