Consider a Carnot Refrigeration cycle with a working fluid of R-134a operating b
ID: 1862139 • Letter: C
Question
Consider a Carnot Refrigeration cycle with a working fluid of R-134a operating between temperatures of -10?C and 20?C. The compressor in the cycle requires 500 W of power.
a) What is the maximum coefficient of performance?
b) What is the rate of heat that is removed from the refrigerated space?
c) What is the rate of heat that is rejected from the cycle?
d) The R-134a enters the evaporator as a saturated mixture with a quality of 0.1. If the R-134a leaves the evaporator as a saturated mixture with a quality of 0.9 what is the flow rate?
Explanation / Answer
For refrigerant R134a
at -10 C
hf1 = 186.7kJkg,hg1=392.66 kJ/kg
sf1=0.9506, sg1=1.7334
at 20 C
hf2=227.47kJ/kg, hg2=409.75kJ/kg
sf2=1.0962, sg2= 1.7180
Now
h1=hg1=392.66,
s2=sg2
Now
since s1<sg2
so point 1 will inside the vpour dome and let x be the quality at inlet of compressor
so, s1=s2
sf1+x(sg1-sf1)=s2g
0.9506+x(1.7334-0.9506)=1.7180
on solving we get x= 0.98
so h1=hf1+x(hg1-hf1)=186.7+0.98(392.66-186.7)=388.54
h2=h2g=409.75
h3=hf2=227.47
h4=h3=227.47
Win=0.5kW
so mass flow rate(m)=Win/(h2-h1)=0.5/(409.75-388.54)=0.0235 kg/s
(a) Maximum COP=T2/(T1-T2)= (-10+273)/30=8.76
(b) rate of heat removal =m(h1-h4)= 0.0235(388.54-227.47)=3.797kW
(c) heat rejected in condenser= m(h2-h3)=0.0235(409.75-227.47)=4.283kW
(d) for this case
h4= hf+0.1(hg-hf)=186.7+0.1(392.66-186.7)=207.3kJ/kg
h1=hf+0.9(hg-hf)=186.7+0.9(392.66-186.7)=372.06 kJ/kg
so flow rate = heat removal rate/(h1-h4)=3.797/(372.06-207.3)=0.0230 kg/s