1. Suppose a temperature sensor has a linear transfer function as v A+ B\'t, whe
ID: 2292906 • Letter: 1
Question
1. Suppose a temperature sensor has a linear transfer function as v A+ B't, where t is the temperature at °C and v is the output voltage. Its output voltage is 250 mv at 100 °C and 450 mV at O °C. (a) Find its sensitivity and the transfer function. (b) Suppose the application requires the sensor to measure temperatures ranging from 10 C to +50 °C. Find the output range of the sensor (c) Design an analog interface between the temperature sensor and the ADC (Analog-to- Digital Convertor). The analog input range for this 12-bit ADC is 0 to 5 V. The sensor output signal should completely fill the ADC input span. Find the transfer function of the interface circuit.Explanation / Answer
1)
v = A + B * t
Given
250mV at 100oC & 450 mV at 0oC
250 = A + B * 100 ........(1)
450 = A + B * 0 .........(2)
From (2) we have
A = 450mV
Putting A =450 in (1)
250 = 450 + B * 100
B = (250-450)/100 = -2mV/oC
Thus, the sensitivity of the linear transducer is -2mV/oC.
Transfer function is
( v - 450 mV)/-2mV = T
b) ouput range of sensor.
First
for 10oC, v = 450 + (-2 x 10)
= 430 mV
for 50oC,
v = 450 + (-2 x 50)
= 350mV
The output range of sensor is 350mV to 430 mV.
c)
The sensor voltage ranges from 250 mV to 450 mV.
The ADV voltage ranges from 0 to 5V.
So, transfer function at interface = ( Range of ADC)/(Range of sensor)
= ( 5 -0) /( 450 mV -250 mV)
= 5/ 200 mV
= 0.025 V/mV
V = A + B*t
0 = A + 0.025 x 250
A = -6.25V
Hence the transfer function at interface is
V = - 6.25 + (0.025 * B)
where B is mV (sensor voltage)
V is ADC voltage