Conditions in one zone of a dual-duct conditioning system are to be maintained a
ID: 2324867 • Letter: C
Question
Conditions in one zone of a dual-duct conditioning system are to be maintained at 75 degree F and 50% relative humidity (RH). The cold deck air is at 52 degree F and 90% RH, while the hot deck air (outdoor air) is at 90 degree F and 20% RH. The sensible heat factor for the/one is 0.65. Assume sea level pressure. In what proportion must the warm and cold air be mixed to satisfy the space condition? If the total zone load is 50 tons, what is the total volume flow rate of air supplied to the zone? Sketch the states and processes on a psychrometric chart.Explanation / Answer
Given inputs
TR = 75 F
RH=50 %
Thot =90 F
RHhot =20 %
Tcold = 52 F
RHcold =90 %
Ts = 14.2o C = 57.56 F
Patm = 101.325
Ws = 0.007
Sensible Heat factor = 0.65
Total zone load = 50 tons
Solution :
hR = enthalpy (airH2O, T = TR, R=RR,P = Patm)
Hhot = enthalpy (airH2O, T = Tcold,R= Rcold, P = Patm)
Hcold = enthalpy (airH2O, T = Tcold,R= Rcold, P = Patm)
hs = enthalpy (airH2O, T = Ts, w = ws, P = Patm)
vs = volume (airH2O, T = Ts, w = ws, P = Patm)
50*200/.9478 = ms*(hR-hs)
Hs = (mhot/ms)*hhot+(1-(mhot/ms))*hcold
Volsupply = ms*vs
HotColdRatio = mhot/(ms-mhot)
SOLUTION :
Hcold =29.57 C Hhot = 47.31 HotcoldRatio = 0.1573 hR = 47.83
Hs = 31.98 mhot = 90.49 ms = 665.9 Patm = 101.325
Rcold =0.9 Rhot = 0.2 RR = 0.5 Tcold = 11 C
Thot = 32 C TR = 24 C Ts = 14.2 VolSupply = 548.1
Vs =0.8232 ws = 0.007
Supply Volume = 548.1 m3 /min
Hot to Cold ratio = 0.1573
pyschometric chart http://www.uigi.com/UIGI_SI.PDF