you may plot, but even if you couldnt plot i would like to see answers, you could use Matlab or EES to plot, and if you did please show me (code. results..)

A vapor compression system for an industrial freezer, must be designed to meet a refrigeration load of Qevap = 7.5 tons at Tc = -25 degree C and TH = 27 degree C. The degree of superheat of Delta T sh = 2.3 degree, degree of subcooling of Delta T sc = 2.3 degree C: and compressor isentropic efficiency of eta c = 0.80 and volumetric efficiency of eta vol= 0.77. The cost of the compressor required by the system scales with the compressor displacement rate according to: where Vdtsp in cfm. The costs of the condenser and evaporator scale with their conductances (UAcond and UAevap: respectively) according to: The conductances of the condenser and evaporator are estimated according to: The cost of the electricity required to run the refrigeration system is ec = 0.10 $/kW.hr and the system runs continuously. Determine the compressor displacement rate, condenser conductance; and evaporator conductance that minimize the overall cost of owning and operating the equipment for time = 5 years while providing the required refrigeration rate at the given conditions. Neglect the time value of money for this problem. Your solution must include plot that displays the operating cost: evaporator cost: system cost (compressor; condenser and evaporator costs) and the total cost (system and operating costs) with the condenser approach temperature Delta Tcond = 5.6 degree C is being fixed). You must find optimal total cost and explain the trend logically

Explanation / Answer

Answer question

function [mdot, f, kW, Tdis, exitflag_m] = compressor(Qevap, Psuc, Pdis, Tsuc, hein);
p=Tchparm;p.dP_HX=1;

% initialization

options_m = optimset('LargeScale','off','Algorithm','trust-region-reflective','Display','off','TolFun',1e-10,'TolX',1e-6);

% oil fraction

tref=refpropm('t','h',200e3,'s',1e3,p.Refname); %IIR reference

funh=@(T) 4.186.*(.388+.00045.*(1.8.*T+32))./((.97386-6.91473e-4.*T)*1e3/998.5).^.5; %kJ/kg K

if Tsuc==0

[rhosuc,hsuc,ssuc]=refpropm('DHS','P',Psuc,'Q',1,p.Refname);

else

hsuc1=refpropm('H','P',Psuc,'Q',1,p.Refname);

hsuc=refpropm('H','T',Tsuc,'P',Psuc,p.Refname);

if hsuc<hsuc1
[rhosuc,hsuc,ssuc]=refpropm('DHS','P',Psuc,'Q',1,p.Refname);

else
[rhosuc,hsuc,ssuc]=refpropm('DHS','T',Tsuc,'P',Psuc,p.Refname);
end

end

[Tdis hdis rhodis]= refpropm ('THD','P',Pdis,'S',ssuc,p.Refname);

% refrigerant enthalpy at condenser outlet and assume isenthalpic expansion

if p.dP_HX==1 && hein==0

%initial hliq with 1kPa pressure drop in each tube and zero subcool and zero superheat to calc mdot guess

[Tcout hcout]= refpropm ('TH','P',Pdis-(1*p.cond.Ntot/p.cond.tube.div),'Q',0,p.Refname);

hoilcout=200e3+quadl(funh,tref-273.15,Tcout-273.15)*1e3;

hcout=p.oilcon*hoilcout+(1-p.oilcon)*hcout;

xein=refpropm('Q','P',Psuc+(1*p.evap.Ntot/p.evap.tube.div),'H',hcout,p.Refname);%r-410a

hevaprefliqin=refpropm('H','P',Psuc+(1*p.evap.Ntot/p.evap.tube.div),'Q',0,p.Refname);

hevaprefgasin=refpropm('H','P',Psuc+(1*p.evap.Ntot/p.evap.tube.div),'Q',1,p.Refname);

elseif hein==0

%initial hliq to calc mdot guess

hcout= refpropm ('H','P',Pdis,'Q',0,p.Refname);

hoilcout=200e3+quadl(funh,tref-273.15,Tcout-273.15)*1e3;

hcout=p.oilcon*hoilcout+(1-p.oilcon)*hcout;

xein=refpropm('Q','P',Psuc,'H',hcout,p.Refname);%r-410a

hevaprefliqin=refpropm('H','P',Psuc,'Q',0,p.Refname);

hevaprefgasin=refpropm('H','P',Psuc,'Q',1,p.Refname);
end

if p.oilcon==0

oilconlocal=0;

else

oilconlocal=(1-p.oilcon)/(1-(1-p.oilcon));

end

T1=refpropm('T','P',Psuc,'Q',1,p.Refname);T2=refpropm('T','P',Psuc+1,'Q',1,p.Refname);

equations=[1 T1;1 T2];values=[log(Psuc)*T1;log(Psuc+1)*T2];constants=equations alues;

A=constants(1)+182.5.*oilconlocal-724.2.*oilconlocal.^2+3868.*oilconlocal.^3-5268.9.*oilconlocal.^4;

B=constants(2)-.722.*oilconlocal+2.391.*oilconlocal.^2-13.779.*oilconlocal.^3+17.066.*oilconlocal.^4;

Tbulb=A./(log(Psuc)-B);

heout= refpropm ('H','T',Tbulb,'Q',1-p.oilcon,p.Refname);

% enthalpy of ref-oil mixture (J/kg) from oil thermodynamic property paper

hoileout=200e3+quadl(funh,tref-273.15,Tbulb-273.15)*1e3;

heout=p.oilcon*hoileout+(1-p.oilcon)*heout;

hoilsuc=200e3+quadl(funh,tref-273.15,Tsuc)*1e3;

hsuc=p.oilcon*hoilsuc+(1-p.oilcon)*hsuc;

if hein~=0

mdot=1000*Qevap/(heout-hein); % refrigerant mass flow rate in kg/sec

else

hoilein=200e3+quadl(funh,tref-273.15,MIT.Teia(i)-273.15)*1e3;

heinguess=p.oilcon*hoilein+(1-xein-p.oilcon)*hevaprefliqin+xini*hevaprefgasin;

mdot=1000*Qevap/(heout-heinguess); % refrigerant mass flow rate in kg/sec

end

if mdot<0;
mdot=0;
end

% moil = p.oilcon*mdot; % mass flow of refrigerant oil [kg/s]

vdot = mdot/rhosuc; % volumetric flow rate

Prat=Pdis/Psuc; % compression ratio

if Prat<0
display ('Prat<0');
end

% calculating power

eta_comb = p.C4 + p.C5*exp(p.C6*Prat);

% itterating discharge temperature

[y,~,~,exitflag_m] = lsqnonlin(@compressor,Tdis,Tdis,p.T_max,options_m);

if exitflag_m<=0

keyboard;

end

Tdis = y;

function result = compressor (y)

% refrigerant properties at compressor inlet

Tdis=y;

% if Tdis> 373 %100+373

% Tdis=373;

% end

[hdis rhodis]= refpropm ('HD','T',Tdis,'P',Pdis,p.Refname);

ns = log(Prat)/log(rhodis/rhosuc);

% calculating frequency

etaV = 1-p.C2*((Prat^(1/ns))-1);

f = (vdot + p.C3*(Pdis-Psuc)/1000)./(p.C1*etaV);

kW_comp = (1/eta_comb)*mdot*(ns/(ns-1))*(Psuc/rhosuc).*((Prat^((ns-1)/ns))-1); % kW

%kW_Loss = 24.0+0.0145*(kW_comp*1000); % W

kW = kW_comp;%+kW_Loss/1000; % kW

hoildis=200e3+quadl(funh,tref-273.15,Tdis)*1e3;

hdis=p.oilcon*hoildis+hdis;

Qcomp = mdot*(hdis-hsuc)/1000; % kW

% equation that needs to be satisfied

result = kW_comp-Qcomp;

end

end

% Tcpharm function

function p=Tchparm;
%% General:
p.Pamb = 101.325; % atmospheric pressure [kPa]

%% Refrigerant Specifications:
p.Refname='R410a'; % refrigerant that is used
p.Refmix1='R125';p.Refmix2='R32';p.Refmixcomp=[.5 .5];
p.airname='air';p.watername='water';p.Pamb=101.325;
p.Mref = 72.585; % molar mass for R410A [kg/kmol]
p.T_min = 142.89;%for two phase region
p.P_max = 500*6.89476; %for two phase region
p.T_max=400; %for single phase region 100+273
p.Pcr = 4.9e3; % critical pressure [kPa]
p.Ptp=30;

%% Oil Specifications:
p.oilcon = 0.01; % precentage of oil in the refrigerant [-]

%% Evaporator Parameters:
p.evap.vertical=.34;p.evap.width=.62;
p.evap.Ntot=32;p.evap.tube.div=2;
% Tube Parameters:
p.evap.tube.row=2;
p.evap.tube.pitchtransverse=20.6375e-3;
p.evap.tube.length=620e-3;
p.evap.tube.Do=6.7564e-3;
p.evap.tube.t=.8e-3;
p.evap.tube.k=400;

%%
% Fin Parameters:
p.evap.fin.t=.1016e-3;
p.evap.fin.w=25.4e-3/2;
p.evap.fin.p=1.27e-3; %18 fins per inch
p.evap.fin.k=235;

%% Condenser Parameters:
p.cond.vertical=.5048;p.cond.width=.889;
p.cond.Ntot=24;p.cond.tube.div=2;
% Tube Parameters:
p.cond.tube.Nliq=4;
p.cond.tube.row=1;
p.cond.tube.pitchtransverse=21e-3;
p.cond.tube.length=870e-3;
p.cond.tube.Do=6.5278e-3;
p.cond.tube.t=.8e-3;
p.cond.tube.k=400;
%%
% Fin Parameters:
p.cond.fin.t=7.62e-5;
p.cond.fin.w=21.96e-3;
p.cond.fin.p=1.41e-3; %20 fins per inch
p.cond.fin.k=235;

%% Chiller Parameters:
p.chiller.plates = 14; % number of plates
p.chiller.plate_length = 0.415; %[m] chiller lenght
p.chiller.plate_width = 0.0858; %[m] chiller width
p.chiller.plate_depth = 0.0425; %[m] chiller depth
p.chiller.plate_thick=.5e-3; %[m]
p.chiller.plate.k=16; %[W/mK]
p.chiller.developed_length= 6.5*2.1*1e-3; %[m] taken in 2.1 finite steps
p.chiller.protracted_length = 12.3*1e-3; %[m] taken in 2.1 finite steps
p.chiller.channel_thickness=2.2352e-3;
p.chiller.corrugation_pitch=6.8e-3;
p.chiller.chevron_angle = 60;
p.chiller.dia_water = 26e-3; %[m] water connection diameter
p.chiller.dia_ref = 26e-3; %[m] refrigerant connection diameter

%% Compressor Parameters:
% Tea's Model Constants:
p.C1=9.20000000000000e-06;p.C2=0.11556185;p.C3=1.52444E-05;
p.C4=-0.090012328;p.C5=1.053942728;p.C6=-0.159224192;

%% Outdoor Fan Data:
%MIT
%cfm= 0.6487*rpm^1.096
%3phpower=1.958e-7*flow^2.703

%MI
%cfm=.739*rpm^1.084
%3phpower=5.093e-9*flow^3.27

%W=c1*x^c2
p.cfanC1MI=383.126;p.cfanC2MI=3.27;
p.cfanC1MIT=191.55;p.cfanC2MIT=2.703;
p.cfanC1=383.126;p.cfanC2=3.27;

%% Fan and Pump Power Exponents
p.cfanC1=191.8;p.cfanC2=2.703;
p.efanC1=431;p.efanC2=1.792;
%p.efanC1= 2.758e+006;p.efanC2= 1.493;p.efanC3=18.63; %for grundfos pump alpha2l-50 with CP2