A piston-cylinder device contains 12 kg of saturated vapor R-134a at 2.4 bar (St

ID: 1861754 • Letter: A

Question

A piston-cylinder device contains 12 kg of saturated vapor R-134a at 2.4 bar (State 1). A 110V electric source supplies current to a resistor within the cylinder for 6 minutes and heat transfer of 300kJ occurs to the system.  During these energy interactions, the pressure is maintained constat and the refrigerant is heated to 70 degrees C (State 2).


a) Calculate the current (A) supplied to the resistor.

b) Show the expansion process for R-134a on a P-v diagram.  Label states, show property values, and indicate appropriate lines of constant temperature.


Thanks for any help you can give!

Explanation / Answer

Answers:

(a) 13.5 A;

(b) Not attached