7. You are hired by CDOT as an engineering consultant to tell the power company
ID: 3280820 • Letter: 7
Question
7. You are hired by CDOT as an engineering consultant to tell the power company where to dig in order to make a repair to a transmission line that is burie insulated metal cables. Each metal cable has a resistance-per-length of 17 CDOT claims th line. The transmission line has access every 13 km where you can make independent nission line consists of two parallel /km. at they are experiencing excessive power loss in the transmission electrical connection to the two wires. (a) What should you expect the current to be if you attach a 120-volt source across the two electrical connections at an access point. (b) When you connect a 120-volt source across the connections at station F, a current of 270 mA flows from the source. When this is done at Station G (the next station 13 km east of Station F), a current of 590 mA flows. You conclude that somewhere along the transmission line between Station F and G, the insulation is damaged, allowing current to flow through the dirt from one cable to the other. Where should CDOT dig up the highway?Explanation / Answer
a)
equivalent resistance of transmission line up to the access point
Req=2*(17 ohms /km)(13km)=442 ohms
Therefore current at an access point is
I=V/R=120/442
I=0.2715 A =271.5 mA
b)
Let X be distance where the fault occurs from station F ,then the voltage across station F is equal to Voltage across station V
VF=VG
(0.27)*(2*13 ohms/km)*x=0.59*(2*13 ohms/km)*(13 km-x)
0.27x=0.59(13-x)
0.86x=7.60
x=8.92 km =9 km (approx)
Related Questions
Hire Me For All Your Tutoring Needs
Integrity-first tutoring: clear explanations, guidance, and feedback.
Drop an Email at
drjack9650@gmail.com
drjack9650@gmail.com
Navigate
Integrity-first tutoring: explanations and feedback only — we do not complete graded work. Learn more.