UNIT 3 Grounding Electroue u of the following statements about splicing or conne

ID: 3348945 • Letter: U

Question

UNIT 3 Grounding Electroue u of the following statements about splicing or connecting a grounding electrode pernitted to splice or connect the grounding electrode conductor only by o. It is permitted to connect sections of copper busbars together to form the grounding c. It is permitted to connect grounding electrode conductors together by using a copper d. Listed wire connectors or exothermic welding is permitted to be used to connect don thot uerr not honded to the grounding electrode 10. Which conductor is not true? a. It is exothermic welding or irreversible compression connectors. electrode conductor. busbar not less than ¼ in.x 2 in. (6.4 mm × 50 mm). grounding electrode taps to the busbar.

Explanation / Answer

Answer is b. It is false that it is permitted to connect sections of copper busbars together to form the grounding electrode conductor. Because the grounding conductor must be continuous in length. If we connecf sections of copper bus bars there will be discontinuities.